I am using a DM register as a total products produced counter using each on/off transition of a photocell to increment DM[n] +1.
This works fine until count 32768 when the numbers display negative and decrements. I am certain it relates to the max value a DM register can hold, but I am uncertain how to overcome this issue.
My HMI reads this register and displays it's value to the machine operator. Any suggestions?
-
I just noticed in the manual that these are 16 bit registers. Any tecniques to work around this obstacle would be welcome.
-
Use a 32bit variable like A-Z then store the upper and lower part of the variable in two DM locations. Look at the SETHIGH16 and GETHIGH16 statements.
-
How many 32-bit variables do you need? There are another sixteen 32-bit variables EMLINT[1] to EMLINT[16] that you can use for this purpose.
If it is not sufficient, then you need to combine two DM into one by adding a bit more codes:
Say DM[1] and DM[2] are used together:
DM[1] = DM[1]+1
IF DM[1] > 10000
DM[1] = 0
DM[2] = DM[2]+1
ENDIF
This way, the total value = DM[2] x 10000 + DM[1]
The maximum count value is 327,670,000 (327 million).
Letting DM[1] rolls over at 10000 make it easier to read but you can increase maximum count by letting it roll over at 32767 which allows up to >1 billion count.
-
How do I reference these additional 32 bit variables in my touch screen?
I am using modbus. I only need on 32 bit register.
-
Unfortunately 32-bit variables in the PLC are not mapped into MODBUS holding register space.
MODBUS only takes in 16-bit number. Your system may refer to a 32-bit number using two consecutive 16-bit modbus register. In that case, then yes, you need to use a 32-bit variable as counter and then use the GETHIGH16 to get the upper 16 bit of the 32-bit variable and store into the adjacent DM so that it become visisble to MODBUS.
-
Thanks to PLC_USER and Tech support for your help.
-
No problem