General => Technical support => Topic started by: Tito on September 08, 2012, 10:50:30 PM

Title: Omoron CP1E N30
Post by: Tito on September 08, 2012, 10:50:30 PM
Hi,
I am trying to establish communication between PLC WebServer (serial port setup) and Omron.

I did set up as follows:-
Comm: com1
Databits: 7
Parity: Even
Baud rate : 9600
Stop Bits: 2
Timeout:500

In command string  : @00MS       'STATUS READ
follow by pressing "FCS"
gives FCS = 5E
than type in command string : @00MS5E*
follow by return key
message prompt : Warning no response form PLC.
i did use the same cable which used in FMD. Please do advice
Title: Re:Omoron CP1E N30
Post by: Tito on September 09, 2012, 06:10:01 PM
 ;D Hi
I did manage to sort out that after re-configure the serial cable according to omron connection using RS232 ports.