Post by: garysdickinson on February 18, 2009, 10:50:47 AM
Is there a way to set/clear the RTC.ERR using ladder logic or custom functions? I'd like to clear this bit after setting the TIME[] and DATE[] variables.

I notice that the RTC.ERR bit is cleared via the "Set PLC's Real Time Clock" diaglog in i-TRiLOGI.

I can load the TIME[] and DATE[] with correct time/data info by use of the <READ RTC> NS command.  The writing o the TIME[] and DATE[] values does not effect the RTC.ERR status.

Ladder logic can use "RTC.ERROR" as a contact but cannot use this bit at the end of the logic as a COIL (output, relay, ...) nor can it use "RTC.ERROR" as the target for a functions (latch/clear/Reset).
Title: Re:Set/Clear of RTC.ERR
Post by: support on February 19, 2009, 12:22:59 AM
If you have r49 or later firmware, then loading a value into TIME[] or DATE[] variable will automatically turn off the RTC.Err light and the bit (I just tested it and it works). Earlier firmware version does not support this.
Title: Re:Set/Clear of RTC.ERR
Post by: garysdickinson on February 19, 2009, 08:50:58 AM
Thanks,

This makes perfect sense, my test board is r42.