I remember reading before that the PLC ID's were only valid up to a limit when using MODBUS RTU. I can't find this reference anymore, could you please confirm what this?
Thanks
-
According to Modbus specifications the ID for a Modbus slave may only be between 1 and 247.
-
Hi, and agreed!
You might be able to handle that many devices. However, if you are using RS-485 network, the RS-485 transceivers may not be capable of driving that many devices in the same network. See http://www.modbus.org/ also see http://en.wikipedia.org/wiki/RS-485 for bias network termination and other details.