I have no idea how to write this custom function..any help please
I want to limit X amount of rpm's over X amount of time
(rpm's = 12 volt pulses)
If rpm's increase more than X from current read rpm's over X amount of time, turn on output 1. Then reset and restart function.
This function will allow me to detect engine rpm abnormal increses and retard ignition timing momentarily to stop wheel spin
Thanks for any help
-
Are you using the T100MD+ PLC? If so, you can wire it to input #3 or #4 and measure up to two channels of incoming pulse frequency using the PMON and PULSEFREQUENCY function. Then it is a matter of IF THEN ELSE statement to compare the current rpm with previous rpm.
E.g. PMON 1 in an init function.
M = ??? ' the normal frequency (RPM*60)
Use a clock pulse (e.g. 1.0 second) to read the frequency of incoming pulses from input #3 (Pulse monitor channel 1):
X = PULSEFREQUENCY(1)
IF (X-M) > ??? THEN
SETIO xxx ' xxx is the label name of output 1.
...
ELSE
...
ENDIF
' IF the current frequency (pulse per second) is an acceptable value then
M = X ' store the normal M value.
-
there is not a normal rpm it will vary from 1000 to 9000.
I want to detect a e.g. 500rpm increase if they occur faster than e.g. 1ms
-
yes t100md but would like to convert to small plc you sell.
-
actually the time base should be .1 seconds
-
M as constant is just an illustration. You can will need to assign the correct value of M.
What you can do is to detect if the measured RPM (which is frequency *60 if you receive 1 pulse per revolution), so what you need to do is to check:
X = PULSEFREQUENCY(1)*60 - M ' M is the RPM
IF X >500 THEN
....
ELSE
....
ENDIF
T100MD+ PLCs or T100MX+ would be the only PLC models we have that are able to execute these codes.
You can read the pulsefrequency evey 0.1s if you wish.
-
NICE!!!!
still a little fuzzy on (M) value...i.e. CORRECT value of M
What this should do is on a race car as the engine accelerates (from 1000 to 9000 rpm) is to check if the engine rpm increases more than 500 rpm in .1 seconds . I want to ignore decelerations
Would PULSEFREQUENCY(1) = (.1) for my circuit?
What is the shortest time base I could assign.... (.01)?
I do in fact receive one 12volt pulse per engine revolution
This is an amazing little box..I have used it for SO many applications.
-
PULSEFREQUENCY(1) means getting the frequency of the incoming pulses on channel 1. On the T100M+ PLC, this channel is mapped to digital input #3. This has nothing to do with the sampling time.
Since the engine produces a pulse every revolution, that means if you measure incoming pulses to be 150Hz, that means the engine is running at 60*150 = 9000 rpm.
So you can add the last measured value of X to M:
M = M+X
So the next time you run the custom function again you will be checking if the new X is greater than the new M
X = PULSEFREQUENCY(1)*60 - M ' M is the RPM
IF X >500 THEN
....
M = M+X ' update the new M value.
ELSE
RETURN ' do nothing
ENDIF
Your sampling time is determined by how often the ladder rung is run. E.g. if you run it with a 0.1s clock pulse then every 0.1s the following function would be executed.
CLK:0.1s Fn_#1
|---||-----------------------{dCusF}
Of course the timing is only accurate if the whole program (ladder logic +BASIC) scan time does not exceed 0.1s.
-
thanks for the ALL the help
I'll let ya know how it turns out
Charlie