i am trying to make a on delay and a off delay run the same output
thermostat on---------------------------------------------------compress on (out)
|
|_____delay on 30 sec___________________Fan on (out)
|
|_____delay off 2 min ------------------------------Fan on (out)
my mind is not yet intune with ladder logic
How do i this simple circuit
it seems to me that the timers need to see a change of state
do i need to wright a custome functionto do this?
please help
-
Ok
Well i got the On Delay to work Still lost onthe Off Delay
Thermostat_____________________________________OnDelay_10
(TIM)
OnDelay_10____________________________________Comp_On
(OUT)
Comp_On______________________________________OnDelay_90
(TIM)
OnDelay_90______________________________________Fan_On
(OUT)
This Works But is it the Rigt way,Best Way and how do i do the Off Delay for the Fan
-
In reference to your original example: I believe this can be done with an interlock. Please check the programming manual for the interlock on, interlock off special input bit. This should accomplish what you have depicted in your first example.
Good luck
plc_user
-
An example of OFF timer is as follow:
ON Out1
|------||--------------------[Latch]
OFF T1
|------||--------------------(TIM)
T1 Out1
|------||--------------------[Clear]