I need read 2 rtd (pt100) sensor with T100MD888+PLC, please give me any sugestion.
Thank alot
-
The quickest means is to buy a commercial PT100 signal conditioner that will output 0-5V, 0-20mA or 0-20mA (the latter two can be converted into voltage by using a 250 ohm resistor) and connect to the T100MD888+'s analog input.
You can also build a two-resistor voltage divider using the PT100 as one of the resistors and construct a simple opAmp to amplify the voltage drop across the PT100 resistance into 0-5V. A sample circuit can be found at the following link:
http://www.tri-plc.com/applications/PT100Interface.pdf
-
We just hooked up an RTD using the diagram from page 6 of the installation guide. Rather than a 1K Ohm Pot, we have a 100 Ohm RTD. (Using T100MD-1616+)
So far it works just fine. This allows us to bypass the expensive converter. Are there any problems with this? Are we going to experience problems later?
-
I assume you are using the RTD in series with a resistor to provide the voltage dividing effect as outlined in the document:
http://www.tri-plc.com/applications/PT100Interface.pdf
The only thing you need to check may be whether self-heating of the RTD may affect the readings slightly, but there should not be any long term ill effect on the connection.