I have a T100MD2424+ that has been in use reliably for about 8 years. I am looking at changing a portion of the machine. I am wanting to know if the 4 HSC counters on inputs 3-6 can be used independantly to to count pulse 4 streams ? I know that 3&4 make a pair for quadrature decoding as do 5&6 I just want to verify they can be split having no count interaction.
-
Unfortunately the HSCs cannot be split into four separate channels since they are organized as two channels of quadrature decoder.
If the incoming pulse speed is not too high (< 200Hz) you may be able to define them as interrupt inputs and each of their associated ISR can be programmed to increment or decrement a variable, which serves as a counter for your program.
E.g. ISR for interrupt input #1 (rising edge) A = A + 1
ISR for interrupt input #2 (rising edge) B = B - 1
etc.