I have an 12-24 VDC supply encoder with NPN outputs that I want to use with a Fx2424 PLC. What is the value of the internal pull up resistor on the Fx2424 inputs to 24VDC which the encoder will have to pull low?
Thanks

 
Title: Re:fX2424 ENCODER INTERFACING
Post by: support on September 08, 2014, 11:34:49 PM
The inputs on Fx2424 are are pulled up to 24V DC via a 5.6K resistors.