Could you tell me what I'm doing wrong! I keep getting
1.1 l/min on the hmi?
( I have a pulse - flow meter that produce's 570 pulse's
per litre) I am trying to average the flow in L/Minute, using a 15 second sample, X 4 = 1 min. I need to display the value on the lcd screen as 1.48 L/Min.. or 2.3 L/Min...ect,what ever the actual flow rate is.. the rest of the process is based on NOT falling below 1.40 L/Min
IF TESTIO(15_MIN_AV) = 0
SETLCD 3,1, STR$(F) + "." + STR$(F MOD 100) + "L/min"
ENDIF
D = HSCPV[1]
E = (D*4)
F = (E/570)
CALL 17
-
If your intention is to use the integer number F to represent 0.01 unit per digit, then you just need to multiply it by 100:
F = E*100/570
....
SETLCD 3,1, STR$(F/100) + "." + STR$(F MOD 100) + "L/min"
this should work.
-
Maybe you would want to try something overly complicated like I did below.... lol :)
setlcd 4,1," "+mid$(str$(gettimersv(4)),1,len(str$(gettimersv(4)))-1)+"."+mid$(str$(gettimersv(4)),len(str$(gettimersv(4))),1)+" seconds "
It will automatically adjust and display the value as a decimal number.
In my case, one decimal point.
In my example above replace the GETTIMERSV(4) after the STR$ in each of the LEN portions with your calculation for flow or however your set your varibale F.
Looking quickly at your code, you display the variable then add a decimal and then add the 100's.
Will it not be displaying the number twice in a sense? What if the interger variable = 148, would it not display 148.8 or something along those lines?
Anybody, any comments?