Am new to this.
Have a T100MD-888+ connected to a EXP1616R. Am writing a proram for this and wondered where the 16 relay outputs will show up--that is what output number I should assign to them in the program, the manual mentions the input numbers to use for the expanded inputs but not the relay outputs.
Thank you
-
A single EXP1616R connected to T100MD888+ will start from output #17 to #32 as well as input #17 to #32. Input #9-16 and output #9-16 are not used on T100MD888+.