General => Technical support => Topic started by: rossi32s on March 01, 2005, 10:42:56 PM
-
E10+ PLC
Trying to get and output to trigger for the first scan only. Im using this to "home" the machine.
I currently have it set to use a momentary switch but this is not acceptable in the final design.
Thanks
Scott
-
E10 doesn't have a first scan bit, but you can use the following emulation:
R1 T1
|---|/|--------(TIM)
|
| T1 R2
|---| |-------[DIFU]
[DIFU]
R1 and R2 are two internal relays. T1 is the timer.
R2 will therefore only trigger for one scan time only after T1 times out and you can use it for homing purpose. T1 can be 0.2 second so that the first scan is trigger 0.2s after the PLC has been powered ON.