Title: Single bit set or clear over comm link
Post by: mundie on September 04, 2002, 04:10:12 AM
Is there a native protocol command to set a single output bit, or must I read the status of the output channel(8bits) and change the bit I want then write the output channel.
Title: Re: Single bit set or clear over comm link
Post by: support on September 04, 2002, 01:26:47 PM
There isn't a native command that let you force a single bit ON or OFF so you do have to read in the output channel, make your changes and write back to the output.

MOBDUS does have a function that affects single bit which is function 05.  You could use the MODBUS ASCII protocol for such a purpose.