I have a time of day based custom function running. I can turn on and off out puts based on time of day and day of week. I am trying to be bale to override the time of setting by seeing if a input is set. When I compile the program , I get a error stating the name is incorrect.
Code is below.
@10 If RLY[1]=1 goto @90
@20 Else
@30 If Date[4]>=1 and Date[4]<=5 and TIME[1]>7 and TIME[1]<16
@40 CLRIO PWR_TV
@50 CLRIO PWR_COMP
@60 CLRIO SPARE_1
@70 CLRIO SPARE_2
@80 Else
@90 Setio PWR_TV
@100 Setio PWR_COMP
@110 ENDIF
-
Your programming example has several problems:
- In your first line, RLY[1] should have been RELAY[1]
- You have two "IF" statements, but only 1 "ENDIF"
- You don't need line numbers (@10, @20, ...) on any line except the target of the GOTO statment.
- You don't need the GOTO statement at all.
- I suggest that you use the TESTIO(x) function to test the state of an input rather than the RELAY[1] mechanism because it is easier to read and to maintain.
The following code is a bit more straight forward and may be easier to debug/maintain:
IF TestIO(Input_X) OR ((DATE[4]<1 OR DATE[4}>5) AND (TIME[1]<=7 OR TIME[1]>=16))
SetIO PWR_TV
SetIO PWR_COMP
ELSE
ClrIO PWR_TV
ClrIO PWR_COMP
EDNDIF