General => Technical support => Topic started by: seitech on September 29, 2003, 07:37:58 PM

Title: PLC Update time/Date Faulty
Post by: seitech on September 29, 2003, 07:37:58 PM
I just connected my new T100MD+ and when I ran the program to update the PLC Time & Date only the Time got updated...no change to the date -1/1/1998.  Any ideas as to fix or is it just a bad PCB.

Seitech
Title: Re: PLC Update time/Date Faulty
Post by: support on September 29, 2003, 10:38:27 PM
The date and time both has been changed. The reason you don't see it displayed on the LCD is because the "clock.pc5" program loaded in the PLC when it was shipped from factory only displays the date once upon power on reset. It does not keep displaying the date so the LCD doesn't show the new date.

What you need to do is to do an on-line monitoring and click on the "View" button and you will be able to see the new date in the Real Time Clock. You can then click on the "Reset" button and this time the LCD will show the new date.
Title: Re: PLC Update time/Date Faulty
Post by: support on September 29, 2003, 10:38:52 PM
The date and time both have been changed. The reason you don't see it displayed on the LCD is because the "clock.pc5" program loaded in the PLC when it was shipped from factory only displays the date once upon power on reset. It does not keep displaying the date so the LCD doesn't show the new date.

What you need to do is to do an on-line monitoring and click on the "View" button and you will be able to see the new date in the Real Time Clock. You can then click on the "Reset" button and this time the LCD will show the new date.
Title: Re: PLC Update time/Date Faulty
Post by: seitech on September 30, 2003, 05:40:30 AM
Thanks for quick response.  I did see new date as you have described.  I'll hit he "Reset" button and am sure all will be fine.  Thanks again for quick repsonse.

Seitech