Internet PLC Forum

General => General Discussions => Topic started by: j on June 11, 2004, 12:06:02 AM

Title: altivar31 torque via can
Post by: j on June 11, 2004, 12:06:02 AM
Hello,

I'm trying to communicate a Beckhoff CANOpen master with 11 Schneider altivar31.

The parameters have been entered in the altivar and now the communication is going OK (I can set the desired speed and I can change the drive status).

the only problem is that I cannot get the torque in any way.

I've parametrized the 1a05 parameter (the pdo 6 mapping) in this way:

---------------------------------------------------------------------------------------
1a05:0:1:0x4 (# of elements)
1a05:1:4:0x60410010 (taking a look to the eds file this is the ETAD)
1a05:2:4:0x60440010 (taking a look to the eds file this is the LFRD)
1a05:3:4:0x20020510 (this should be the LCR (current))
1a05:4:4:0x20020610 (this should be the OTR (torque))

---------------------------------------------------------------------------------------

the curious thing is that I don't understand why the bolded ones seem not to be ok, I receive this message when I try to start up the new configuration:

BoxState: SDO data mismatch at StartUp
SDO-Upload-Error 0x 1a05, SI 3: expected value: 0x20020510, received value: 0x0
1 Emergencies stored


does anybody know why?

Do I need to do anything else before?

NOTE:
If I put a 0 there, then I get the same message for the index 0x20020610...

Thank you in advance.
Title: Re:altivar31 torque via can
Post by: support on June 11, 2004, 10:31:10 AM
The Technial Support forum is only for users of TRi PLC and peripheral products and hence this is moved to "General Discussion" board.
Title: Re:altivar31 torque via can
Post by: Jakaaa on January 19, 2009, 08:41:54 PM
Moin,

this Problem is a killer I spent 1 Week to fix it.
You have to go as per Beckhoff help for EL6751
see picture


if you have Questions --> Email
jakob.teurer@devro-casings.com