27
« on: January 16, 2014, 03:13:28 PM »
Good day everyone,
I'm creating some rung to handle emergency hammer buttons. The idea is when the N.C. hammer button is hit, a relay keep the status (latch) and when the hammer button is resetted, a timer start to clear the error status and also a reset error request... the idea is to avoid removing the alarm directly.
The current logic is working fine up to the point when the timer reach 0 (elapsed reset time), the system is waiting a realise relay hit to clean the emergency.
when, under ITrilogi V6.47 I quickly hit the Stop_button_Rel (R71), it's going back in the timer waiting loop...
if I longer hit the Stop_button, then it's correcly clearing the alarm and working as expected.
I cannot explain why a short hit is not clearing the alarm and where it's happening in the ladder. Is it a ladder logic mistake? Where is the fault?
Description of the differents inputs/relay/timers
I1 : INPUT : Emergency_Butt ( N.C. circuit)
R72 : RELAY : Stop_Button_Ok ( Use to be N.C / N.O independant from the INPUT logic)
R70 : RELAY : Stop_Button (Latch that keep that an emergency event happend)
R71 : RELAY : Stop_Button_Rel (Request for cleaning the alarm (If the Stop_button_Ok is not ok, the R71 is opened)
R73 : RELAY : Stop_Button_Tim (Closed when the T2 timer is running)
T32 : TIMER : StopButtonDelay (Set to a amount of waiting time and activated when the physical alarm is cleared)