Hi There,
I am using some T100MD888 units as simple polling devices, with only 3 input and 3 outputs active and a 24 V power supply. Now I would like to connect 2-3 PIR sensors ( from www.parallax.com) - a neat little unit that requires 3.3 to 5 volt for operation and draws < 100uA
I can se that there is a 5 volt output on the Analog connector (which I am not using. Can I use as supply for my PIR sensor?
/Peter
-
if the current consumption or PIR is so low (100uA as you mentioned) then there is no problem using the analog 5V power output, which can deliver up to 10mA.
-
Great Thanks, "<100uA" is what the manual states, so I'll try