I have 18 flow sensors, so some are being read off the PLC (via AN20MA-2) and the rest off the 7017s, one of which is co-located with the PLC and the other two are some distance away on a different part of the property.
Communication with each 7017 happens during a different second, but other custom functions run during the same seconds as the 7017 communication. I've tried to space things out evenly, but it clearly isn't working at the moment.
I'm open to suggestions, including different PLC equipment or communication protocols. One thought I had: use an FMD88 to replace the 7017s. I could multidrop them just the same, but do some remote calculations and send the calibrated data, thus processing remotely and freeing up some processing space on the main F1616-BA.
Ideally I would handle the problem through more efficient code, but if it means scanning the sensors much less often then I want to have an alternate option for the client, one which would allow the high scan rate we originally discussed.

And in case I sound unappreciative, I want to once again thank support and Gary for all the help with this project. It?s been fun learning all this stuff and I'm considering automating and datalogging my own apartment!

Geeze ???, just ran another 30min test and this time the counter is where it should be, implying no lag. I'll let it run over the weekend and see how it does.

17
Well, it didn't take long for the problem to be noticable. I set a counter which would increment within one of the functions  every 5 seconds. After about 30min it was more than 60 counts BEHIND what it should have been. Back to the drawing board.

18
In Gary's code for talking to 7017s he has a re-try routine built in, I think it does 5  total commands of NETCMD$. If each NETCMD$ command already does 3 tries before stopping, then Gary's code will try 15 times before giving up for a total of 2+ seconds. I don't want this, and maybe will just rely on the built-in 3 attempts totaling 0.45s, but keep the part that stops trying to communicate once a 7017 times out from the default 3 attempts.

My problem with any interupt is that I'm reading flow sensors through the PLC and through 3 different 7017s. Reading the 7017s over the RS485 is one of my slow processes, which means it's the most likely to get interupted. For most of the other functions, if they are interupted it will result in incorrect calculation of total flow. The rest of your suggestion is what I'm already doing, reading flow once every 5 seconds and adding the volume to a total volume variable. As long as this occurrs every 5 seconds reliably, I'm calculating flow as I need to. (Pulse flow meters are much better for total flow, but that's not what the client wants!)

19
I haven't learned how to use the built in coils for: counters, sequencers, timers, except for the Clk: ones that I'm using. I will learn what I need to, if I need to, but at the moment it appears that splitting up the actions into 5 different seconds of a 5 second cycle is doing the trick. Although, I'm not done writing the program, so I'm not out of the woods yet.
I would have to look more closely, but I don't think any of my functions can be skipped if one function takes too long to execute, so using an interrupt just moves the problem around.
My flow meters (and at this time all my sensors) are 4-20mA analog signal. I think this allows me to avoid leaning Pulse-* commands for now, as I can't use them with the sensors that are already bought.
However, I'm trying to read the output every 5 seconds and apply the observed flow rate to the previous 5 seconds to compute volume. If the PLC falls behind real time then I'm not calculating the flow volume correctly anymore. At that point it's better to go to a 10-second cycle giving each of the 5 parts 2 seconds to run, or have 10 parts at 1 ssecond each.
I think it's time to write a piece of code that compares the number of cycles to the number expected over a longer period of time. The weekend is coming up, a perfect time to test!

General questions about efficient coding:

Is it better to us "AND-OR" or to nest the IF statements?

If I have many "IF" statements that are normally false (testing for problems) do these statements get processed very fast?
The idea is to build a nested structure with the least likely "TRUE" test at the top, so that the least amount of the nested structure gets analyzed at any pass through. The downfall is that this will take more lines of code because I will have fewer nested IFs within each IF statement.
 (I should have paid more attention in school when they talked about efficent coding practices.  :(  )

My code is only 2000 lines so far, and I think the biggest limitation is reading over the RS485. If I find I still have problems with inefficient code I'll ask more questions about how to streamline what I'm trying to do. Thanks for all the help!

20
Running the HMI I/O as direct ladder rungs works great. No more lag in keystroke pickup.

After splitting up the code so that some things run on the first second of a 5-second cycle, and some on the 2nd second, 3rd second, etc. I was still not getting a read on the 7017s. I noticed one line of code in the sample code for the 7017 that I hadn't given much thought to. The first line of function 250 is "SetBaud" Comm 3 to 9600, which is what the 7017s are expecting. The default Baud rate for the RS232 and RS485 is 38400 for this PLC so adding this line to the 1st.Scan function is needed to properly communicate with the 7017s.

Is it likely that increasing the Baud Rate would allow me to go back to my original code where everything runs every second?

21
Hi Gary, thanks for the response.
We are automating an irrigation system. The tank levels don't change quickly, but the flow sensors do. We are using flow sensors that output flow rate, and applying that rate over time to get flow volume. On the one hand we would like to scan the rate very often to capture abrupt changes in flow that occur when a valve opens and pipes fill, on the other hand converting rate to volume leads to a "rounding" error every time you do it so doing it less often reduces the rounding error. I guess if I'm taxing the PLC then that is another reason to scan less often.
I can convert the HMI to ladder logic, and I can implement your RETRY code for the 7017. You have suggested to stagger the 7017 readings. One way I can think to do this is to run the Clk1.0s and use a counter with an IF statement to run each one on a different second. In fact, I can split up the reading of all the other sensors too, so only 1/5th of the code runs per second. Is there a better way you can think of doing this?

In your description of the ADCError you say you, "do not want my PLC to lock up polling dead hardware." Do you mean waste time, or is it possible that the PLC will become unresponsive and stuck? Also, if that relay is tripped does your program stop trying to read from the 7017 for all future scans?

I have a Clk:1.0s that runs every time and others that run when in a particular State. Is it better for these to be on separate ladder rungs? I could combine them into one rung with TestIO for which state is active if that would avoid problems.

I'm hopping support will answer my question of what happens with multiple rungs of Clk:1.0s when the functions take longer than 1.0s to complete. Is the lower rung just skipped? Or does the program as a whole stop running in real-time while waiting for functions to finish? Or are certain rungs skipped depending on what time it is when an above rung completes the function? Any one of these will cause problems in the code I have, but if I know which one I can change the code to avoid problems.

22
I made some changes in the code and the keystroke issue has gone away, and the CLK:0.1s incrementing counter is now running at a speed which matches real-time.

I've added some LCD output which gives a success or fail message to the LCD. The response from each I-7017 should appear on a separate line. From this I have found I'm not getting a response from the 7017 which should print to the first line of the LCD, but I'm not getting anything on the other two lines. Now that I'm already suspicious of the PLC for the above mentioned reasons, I can't think about what else it could be.
Also, since I don't know what I did to reduce the problem, it's possible I'll commit the same mistake again, and suspect the PLC again, until someone tells me I'm being ridiculous.

23
I have a program that runs alright in the simulator, but not on the PLC(F1616-BA). I have 5 functions which run on the CLK:1.0s every time, State independent. There are some loops in there and a reading of 3x I-7017 over RS485. I also run an adaptation of the HMI sample code which runs every CLK:0.1 when State 1 is active.

One problem is that I'm not getting any reading from the I-7017s, even with a few sensors attached which work when the PLC is running the (much smaller) I-7017 sample code altered to read three 7017s at a time.
I also find that the HMI keystrokes require an unnaturally long depression of the key before they register, and then stay registered for a moment.

I was trying to think how I could have taken working code and corrupted it during cut/paste when I noticed that a variable which should increment every 0.1sec (off CLK:0.1s), was in reality incrementing much slower than that. After 60 seconds in real time, the counter represented 11 seconds. This makes me wonder if my code is causing the PLC to be in mid-execution of some part of a function when the CLK:1.0s forces it to go elsewhere. Or, just as bad, that the PLC continues what it's doing and ignores the request from the CLK:1.0s.

Can you please help me narrow down the possibilities?

Edit: improve clarity and spelling

24
Technical support / Re:Assistance Needed
« on: May 07, 2012, 03:30:03 PM »
Hello gthomas,
I'm fairly new to all this as well, but I think I can be of some help.
First, are the LCD displays much different than the ones sold by TRi? If so, a link to a data sheet will help us understand what you are trying to achive.

For the LCD displays TRi sells, I would do the following:
If each thing you want to count can be measured via one of the PLC's digital inputs, then you can have a simple program that runs each time the input recieves a signal. For example, if a "stroke" is monitored by the proximity sensor you want the sensor to temporaraly close the Digital Input on the PLC. If that is connected to Digital Input 1, then the ladder code is something like:
--||--i1-----------------------------------------------------1-----{dCusF}
normally open input 1                                             custom function #1

and the function would include
x = x + 1 'Where x is the number of counts at input #1
as well as something to update the LCD screen
SetLCD 1,1, "Count for #1 =" + STR$(x)
Which translates to:
On line 1 of the LCD, starting at position 1, print the words "Count for #1 =" and the value of x.

I don't think there is a non-function way to display things on the LCD, so you might as well do the counting in the same function too.

Now, you have more than 26 proximity sensors, so you can't use letters for all of them. In this instance, replace "x" with the other type of variable used, which is DM[1]. I think you can use DM[1] through DM[4000] for a F1616, but at the very least you can use up to DM[1000], which is more than you need. For Digital Input #1 replace "x" with DM[1], for #2 use DM[2] etc.

And to keep a grand total, in each function you can have:
DM[999] = DM[999] + 1
so that anytime one of the sensors sends a signal, it also increments DM[999], keeping a count of the total number of strokes on ANY sensor.

25
That did it, Thanks!
I was thinking that the 10 pin connector marked "Reserved" in the F1616 manual was "reserved" for the keypad. Clearly I was wrong.

Thanks for all the help support. It really makes a difference for someone like me just getting started working with all these new products.

26
I have a similar set-up:

F1616-BA
MD EXP 1616R
MD-HMI

I tried the sample code in the zip file for the HMI, but the keystrokes didn't register. I tried each sample program, then wrote code:
DM[3901] = INPUT[1]
DM[3902] = INPUT[2]  ' Get data from input #17-32
DM[3903] = INPUT[3]
DM[3904] = INPUT[4]
DM[3905] = INPUT[5]
DM[3906] = INPUT[6]
DM[3907] = INPUT[7]
DM[3908] = INPUT[8]

And watched the "View" of the DM fields as I tried different keys during realtime monitoring. Nothing showed up using short and long keystrokes.

I checked the ribbon at both ends, and I know I'm getting power to the LCD at least because I see the "Z$=" displayed.

What else can I do to test how to recieve the HMI input?

27
Technical support / Re:RS485 with 7017
« on: April 24, 2012, 03:57:30 PM »
I'm working with JR on this project so I'm going to continue a line of questioning in this thread.

We will be using the I-7017 at more than 10ft away from the PLC, so we will need the pull up resistor set-up. For the RS485 line power I see we need 9V, and I believe that can be 5-9V. I have my F1616 Analog ports connected to a AN20MA-2, so I've given up my 5V voltage source from the analog port. I think my next best option is to purchase a transformer to power the I-7017. I will have three of these I-7017 multi-dropped at different locations.
---What is the current requirement of the pull-up resistor set-up?

For this set-up I will also need resistors. The resistance I need is shown on the diagram, but my local electronics parts store also asks what wattage the resistor needs to be. I've tried to figure this out, but related to the above question, I don't know what currents I'll be dealing with.
---What wattage resistors do I need, or should I just buy them all at 1W to be safe?

I followed the TRi manual for connecting to an I-7017 using the U-485 USB to RS485 to connect to the PLC. The directions in the TRi manual can't be followed because the I-7017 website has since been updated. I downloaded DCON Utility, but the utility window looks nothing like the sample image in the TRi manual. I was able to connect, but I wasn't able to change the ID of the I-7017.
---Will you please update the TRi manual for the I-7017. At the moment I'm most interested in how works with the F1616, but foresee needing to use it with an FMD88 or other PLC from TRi.

Thanks!

28
Technical support / Re:Are there limitations to DM significant digits?
« on: April 03, 2012, 02:52:47 PM »
To answer my own question:
Variables A to Z are 32 bits in length, allowing -2^31 to 2^31 while DM[] variables allow half the size, numbers -32768 to 32768.

Thanks TravisB

29
Technical support / Are there limitations to DM significant digits?
« on: April 03, 2012, 01:51:14 PM »
I am using an FMD series PLC to read a pressure sensor. In order to get the number of significant digits I need for accuracy, I have to use very large numbers (1,000,000.) My proceedure works when using "letter variables" but not when using DM[] variables. I thought there might be a limit to the number of significant digits for a DM[] variable, but I can't find any mention of this, so now I'm confused.

Sample:
'---Read Main Tank water level
A = ADC(1)       'Tank sensor raw output
DM[11] = ADC(1)
'Calibrate the reading
'These sensors output values on the order of 1000 / foot,
' so to get acuracy of 1/10th of a foot we need to convert to
' 1/1,000,000 to calibrate, then convert back to 1/100th of a
' foot before moving on in the program
B = 2658             'Slope (1/1,000,000 feet)
DM[12] = 2658
C = -2120000             'Intercept (1/1,000,000 feet)
DM[13] = -2120000
D = B * A + C     'Calibrated water level (1/1,000,000 feet)
DM[14] = DM[12] * DM[11] + DM[13]
'Convert back to 1/100th using MOD to trim unwanted sig.dig.
DM[100] = (D-(D MOD 10000))/10000
DM[101] = (DM[14]-(DM[14] MOD 10000))/10000
DM[102] = ((DM[12] * DM[11] + DM[13])-((DM[12] * DM[11] + DM[13]) MOD 10000))/10000
D = DM[100]       'Calibrated water level (1/100 feet)

"D" gives me the correct value, DM[101] doesn't get calculated, and DM[102] returns an incorrect value. (They should all be equal.)
Do DM[] variables keep fewer significant digits that "A, B, C" type variables?

30
Technical support / Re:Way to advance the time/date in the simulator
« on: March 26, 2012, 11:29:15 AM »
Thanks Gary, and thanks support!

Works wonderfully.