General => Technical support => Topic started by: andy22 on February 05, 2010, 03:37:51 PM
-
Hello,
I have a problem with the connection to a E10NPN
cable must be Ok because I can communicate with the T100MD
as software I have WinTrilogi v 3.52
Can You please help me,
Thanks in advance
andy
-
Did you got to the "Serial Port Setup" and select the correct COM port? E10-npn default baud rate is 9600 bps, 8 data bit, 1 stop bit and no parity. Try to enter "IR*" at the command box and if you get a response such as "IR01*" then the communication is OK.
-
WOW
Thanks very much, it MOVES
Andy