The M-series READMB2 command is limited to reading 16 registers. Has this been increased for the Nano or F-series? I need to read 250 registers from 4 devices and I'd rather read them, for instance, 100 at a time.
Thank You.
-
The current limit of READMB2 command for Nano-10 and F-series PLCs 32 words per read command.
-
Similarly, when the M- or F-series is acting as a slave, how many registers can be requested at a time by the master over RTU or over TCP?
Thank You
-
As a Modbus RTU or Modbus TCP slave you can access 122 data point max.
As a Modbus ASCII slave you can access only half the number (61).