Title: Do you support OPC ?
Post by: ayman on December 10, 2003, 10:56:20 PM
DO you ?
Title: Re: Do you support OPC ?
Post by: ayman on December 12, 2003, 07:24:27 AM
My question in other words ( if it's not clear ) :

Is there an OPC server for your hardware ?

The anser is important to me .
Title: Re: Do you support OPC ?
Post by: support on December 12, 2003, 08:32:48 AM
We don't have our own OPC server for our hardware. But there are generic OPC server on the market that have been used successfully with our PLC. If you like more info, you can contact our Canadian distriutor DCI Technologies who is selling an OPC server that works with our PLC.

Contact:

DCI Technologies Inc:   Tel: 1-403-720-4885
Contact: Ted Skinner
URL: http://www.dcitech.com
Title: Re: Do you support OPC ?
Post by: ayman on December 12, 2003, 06:53:49 PM
ok

I knew that your plc supports  modbus protocol , so :

can I use a ( modbus protocol server ) ??

I may be wrong ( technically ) so please tell me if my idea is right or wrong !!

thanks .
Title: Re: Do you support OPC ?
Post by: Christian Ziedins on December 22, 2003, 03:01:08 AM
For me it works well using the Matrikon OPC server for Modbus.