When I activate the ADC command and the 0-5v sensors are not connected the value slowly rises to 4096, i e 5 volts. If a wire to a sensor should break the same will occur? As these sensors can trigger a shutdown alarm when a preset value is met, if a wire breaks then the value will rise and meet the setpoint and cause a shutdown.
How can I avoid this??
-
If such a situation is a concern then using a biasing pulldown resistor is recomended. Assuming your transducer is actively power it will have an output impedence of no more than 1000 ohms, more likely 10 - 100 ohms. If you use a biasing resistor of atleast 100 times (Preferably more) that figure then you'll be introducing very little distortion, especially if the bias supply is say -5 volts.
Evan