General => Technical support => Topic started by: Jane on October 05, 2011, 10:14:21 PM

Title: analog data....
Post by: Jane on October 05, 2011, 10:14:21 PM
Hi,
I am looking on some help to get the function.
On the T100MX, all the A/D are normalized to 12-bit with a range of between 0 and 4096 .  If There are real min data and real max data, Are there the function that the value(between 0 and 4096) is converted to real data.
 i had used to make function to calculate real data.
Title: Re:analog data....
Post by: support on October 06, 2011, 08:50:03 AM
Please refer to the following FAQ thread on how to scale the analog readings to real world data:

http://www.tri-plc.com/yabbse/index.php?board=2;action=display;threadid=349