General => Technical support => Topic started by: mace123s on April 22, 2016, 05:09:40 AM
-
F2424 Processor
Is there any way to see the current Set Value of HSC1
I can get the Preset Value but not the actual set value of the HSC
Thanks
-
Do you mean the current value? You can go online monitoring and click on View Variable button and you will see the 3 HSC values being displayed on the first page of the View Variable screen together next to the integer variables A to Z.