151
Technical support / Re:Analog input to T100MD-888+ ??
« on: June 20, 2005, 07:28:31 PM »
Yes the fuel sensor is a basically a variable resistance with 90 ohm empty, and zero ohm full.  It is only 2 terminals, not 3 like a pot. I was trying to limit the 5 volt reference current to less than 4ma (less than half the 10ma limit without changing RA3) to allow some capacity for other sensors. Then resistance to ground then needs to be around 1K ohms to ground, so the total resistance is 1090 ohm at empty, and the voltage measured zero to .41 volts.  The .41 is 8% of the ADC 5 volt full scale and 4096 * .08 / 4 = 84 steps, which is acceptable. I would prefer to have more current of the 5 volt reference available for other sensors, but think I could live with that.  If my thinking is off, don't hesitate to comment.

Someone has suggested using an OP AMP, which I am learning with a little help. At this point my expertice is a little more than E = IR, just enough to be dangerous, but I can see far enough to build up a breadboard and see what happens.   :)

152
Technical support / Analog input to T100MD-888+ ??
« on: June 19, 2005, 07:11:49 AM »
I have a Tri-Plc T100MD-888+ PLC. It has Analog 0 - 5 volt input, and 5 volt reference voltage available. I have a fuel level sensor that is 0 - 90 ohm range to interface, only need around 50 or so steps, and can handle calibration/non-linearity with lookup table or Basic programing.  Presently there is 30 feet of Cat-5 cable in metallic conduit  to the remote location, I would prefer signal conditioning at the PLC end of the cable.

Also what would be the easiest way to get temperature readings, say -30F to +130F, nearest degree resolution would be more than enough.

Spent all the budget on the PLC, buying a $250 signal conditioner is not an option.

153
Technical support / Fuses & Grounds for T100MD
« on: June 03, 2005, 06:37:10 AM »
I have a T100MD-888+, MD-EXP4040, and a MD-HMI. The T100 manual shows a 1 amp fuse for the T100MD, but no fuses are shown for the other boards. Should the other boards be fused,? value?, parallel fuses?, or one larger fuse for all?  Of course all going to the same power supply, mine happens to be 12 DC.

On the T100MD-888+, the high current ground - all in/output grounds (returns) should go there, to an off the boards ground point (with short proper capacity (amps) wire)  with the exception of the TTL & Cmos in/out on the MD-EXP4040 which have their own grounds on the headers.
 :)

154
Technical support / Re:RS-232 COMMUNICATIONS
« on: April 27, 2005, 06:55:45 PM »
I thibk I have it isolated the issue. All indications were that Zonealarm firewall was disabled, but apparently was not. The firewall was blocking "Javaw.exe". Either by turning off the firewall, or adding "Javaw.exe" to programs access trusted only,  127.0.0.1:9080 seems to be working OK. Thanks for the good support.

155
Technical support / RS-232 COMMUNICATIONS
« on: April 25, 2005, 06:09:36 PM »
Have a T100MD+, trying to communicate with serial port to PC.  From TL server 2.1 am able to set port, and with command string IR*, get appropriate response.  Then from Trilogi 5.3 try to set PLC clock, and after clock settings window get "log in to TLServer" window, where it wants IP address. I must be missing something dumb. :)

156
Technical support / Re:UPS for PLC controlling standby generator
« on: April 21, 2005, 01:41:36 PM »
The 12 volt selected since everything else is 12 volt, sounds like an UPS is the way to go. Thanks for the quick replies, good support!

157
Technical support / Re:UPS for PLC controlling standby generator
« on: April 17, 2005, 03:38:27 AM »
Yes, the lead-acid battery is used to start the generator, but it's a gasoline 27 hp., 2 cyl. Kohler engine. No load battery voltage is 12.7 volts, cranking 12.0 volts. The battery is severely oversized with respect to the engine for normal applications. Was thinking the battery is there, and kept charged, why not use it as the UPS, and eliminate one more piece of equipment to maintain (a separate UPS), but maybe that's a better way to go, a UPS meant for a PC could easily bridge the power outages and aren't that expensive. I was thinking an electronic relay circuit controlled by the 120 volt supply would switch quick enough to keep the PLC from resetting .

158
Technical support / UPS for PLC controlling standby generator
« on: April 07, 2005, 06:55:10 PM »
I Have a PLC (Tri-PLC T100MD888) that will be managing a Tri-Fuel standby generator. Normal power for the PLC will be a 120 VAC to 12VDC linear power supply. The 120 VAC will either be power company or from the generator. There is a delay between switch overs of up to a minute or more. The generator power supply is a 12VDC lead acid battery that will be charged and maintained by the generator's charging system and a 120 VAC charger. The issue is, the brief period while the generator comes up to speed, or switching back to power company power, the PLC needs to remain up and running, otherwise when it would reset, the generator would stop, and oscillation between power sources would result. Have thought about parallel diodes, but the lead acid battery and charges could frequently have voltage above the 12VDC linear power supply. How can I keep the PLC from resetting?  :)

159
Technical support / 60 hz frequency and voltage sensing
« on: March 15, 2005, 02:50:48 PM »
On a T100MD888, how would I measure the frequency and voltage of 120/240 volt 60 HZ power using the pulse width and ADC features of the PLC. Object would be to set alarms if out of range.  :)

160
Technical support / T100MD100 with 12 volt power
« on: March 15, 2005, 02:46:45 PM »
With T100MD100, MD-EXP4040, and MD-HMI, are there any issues with usung 12 volt power. On the MD-HMI, the 15 watt resistor for backlight, should it be a different value?

The application is controlling a tri-fuel standby generator, and the backup PLC power will be the generator's 12 volt battery. Will brief interuptions in the PLC power , like when a relay (coil from 120 volt power) drops to the battery supply. The brief period of inactivity is not an issue as long as the PLC at worst resets and then continues. Is there a better way to handle the power change over?

161
Technical support / Start event every "n" (1-4) weeks
« on: February 14, 2005, 03:38:49 PM »
With a T100MD888, how would I start an event every "N" weeks. The application is an exerciser for a standby generator.

Also assuming with Basi will be able to display time, day, date on attached display.  :)