I'm currently testting the T100MD with the Matrikon OPC server for Modbus.
I can't find a way to force one single output bit without forcing the whole row (the 16 bits)
The manual (page 5-3) seems to suggest that modbus function code 05 (force single coil) is supported.
A possible workaround would be: read the whole row --> do an OR calculation --> send the result back......if no better solution I will stick to this one but I don't like the idea of overwriting the 16bits each time..
Any suggestions ?
Cheers,
Christian
-
The M-series PLCs do support MODBUS function 05 which is to force set/clear a single output bit. However, your OPC server must support function 05 in order to do so. The bit address in this case can be found in the following link:
http://www.tri-plc.com/appnotes/modbus-map.pdf
This is an updated document of Chapter 5 of the user manual which now include the document on the Bit addressing. To turn ON output 1, execute a Function 05 at address 257.