Author Topic: MD-HMI420 cables  (Read 10586 times)

Bruceh

  • Newbie
  • Posts: 22
  • a llama no longer !!
    • View Profile
MD-HMI420 cables
« on: September 05, 2006, 05:01:39 PM »
Can you tell me how long are the two cables that the HMI420 is shipped with?
10-way ribbon cable to expansion connector
14-way ribbon cable to LCD port

Many thanks

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:MD-HMI420 cables
« Reply #1 on: September 05, 2006, 05:23:09 PM »
They are both 3 ft (approx 1 metre) long. You should not lengthen       the cable as the low voltage logic signal will be easily affected by noise and transmission line effect when the cable are extended for longer than designed spec.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

Bruceh

  • Newbie
  • Posts: 22
  • a llama no longer !!
    • View Profile
Re:MD-HMI420 cables
« Reply #2 on: September 05, 2006, 05:54:31 PM »
Thanks for prompt reply!
1m is plenty - I promise not to extend it