T100MD+ as tacho/pulsefrequency
« on: August 01, 2006, 07:32:32 PM »
I am trying to configure my T100MD+888 to take an input from a hall effect sensor providing a square wave output.

The first line of my program has the " first scan" bit and then a fuction box where " PMON 3" is written.

The second line has the "clock 0.05s" bit and then function box where "DM[1] = PULSEFREQUENCY (3)" is written

When I write to the PLC and test the DM[1] value is always at zero, i have a few different inputs ie dig in 3 pulsed straight to ground instead of using the sensor, but nothing works

I am pressuming I am not programming it correctly.

Can anyone suggest anything?

Thanks

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:T100MD+ as tacho/pulsefrequency
« Reply #1 on: August 01, 2006, 07:36:27 PM »
try PMON 1, not PMON 3. Frequency measurement channel 1 is mapped to input #3. See page 1-2  of your user's manual for details.

Email: support@triplc.com
Tel: 1-877-TRI-PLCS

CMS

  • Newbie
  • *
  • Posts: 18
  • I'm a llama!
    • View Profile
Re:T100MD+ as tacho/pulsefrequency
« Reply #2 on: August 01, 2006, 08:28:07 PM »
Thanks

That did the trick