Author Topic: ANALOG OUTPUTS RISING TO 4096 N/C  (Read 5498 times)

CMS

  • Newbie
  • *
  • Posts: 18
  • I'm a llama!
    • View Profile
ANALOG OUTPUTS RISING TO 4096 N/C
« on: July 30, 2006, 11:45:27 PM »
When I activate the ADC command and the 0-5v sensors are not connected the value slowly rises to 4096, i e 5 volts.  If a wire to a sensor should break the same will occur? As these sensors can trigger a shutdown alarm when a preset value is met, if a wire breaks then the value will rise and meet the setpoint and cause a shutdown.

How can I avoid this??

evanh

  • Jr. Member
  • Posts: 59
  • y=A+B*(1-cos(2*Pi*x))
    • View Profile
Re:ANALOG OUTPUTS RISING TO 4096 N/C
« Reply #1 on: July 31, 2006, 04:12:13 AM »
If such a situation is a concern then using a biasing pulldown resistor is recomended.  Assuming your transducer is actively power it will have an output impedence of no more than 1000 ohms, more likely 10 - 100 ohms.  If you use a biasing resistor of atleast 100 times (Preferably more) that figure then you'll be introducing very little distortion, especially if the bias supply is say -5 volts.


Evan