Thanks for the speedy reply.
The voltage on the RTC when powered ON is 4.966 Vdc, and OFF 3.151 Vdc.( Pins 14 and 28 )
Input power to the PLC ( on PLC terminals ) is 11.89VDC
When the unit comes in for repair, I run it from a 1.7 amp regulated bench supply
The installation on the vehicle includes a 3 amp 3EQ1 EMI Filter in series of the power leads.
Today, I let the current unit run for about 2 hours ( bench supply ), and went to lunch. when I returned, the LCD was blanc, and attempting to do online monitoring, gave me the same error message as before. That the Checksum Test failed,
In trying to Reset the PLC through the Online monitoring screen, I received a series of Runtime Errors in all the custom functions with a System Variable Index out of range.
i.e Runtime Error in Fn#1, System Variable Index out of range
then pushing the Reset again, I would get Runtime Error in Fn#2, System Variable Index out of range. The rror was the same, cycling through several Custom Functions.
This unit is reporting r49 as its firmware version.
On these units its Dip switch #1 ( SW1-1 ) that is turned ON ( for data retention when the unit is disconnected from power) , not #4. Have the DIP Switch functions changed?
Remember we have been operating without a problem for a year with the two that have failed, and there are units out there that have been operating longer without a problem, and with the same input power design. ( 3eq1 Filter ). I am fully aware of the electrical noise on vehicular systems, but if this was a consistant problem, I would have had more failures, and sooner.
My understanding would be when the unit is powered up, the program in the EEPROM is loaded into the RTC SDRAM. Do I assume the Checksum test is performed after this, and compared to one stored in the EEPROM? Is this value then stored in SDRAM? because my second failure today occured while the unit was running.
I added the SETSYSTEM 5, 3999 statement, and reprogrammed the system again. I'll leave it run this afternoon.
Typically when I set these systems up, I will let them run for 48 Hr, with a simulator, to check the calander clock, and DM
- memory retention, powering on/off at least 4 times during that 48 Hr. period.
I have a complete spare T100MD here and would like to replace the MX-RTC and or the EEprom. Which should I replace first?
Thank you for your assistance