Author Topic: Timer Set Values  (Read 5490 times)

RobertK

  • Newbie
  • Posts: 4
  • I Know Nothing!
    • View Profile
Timer Set Values
« on: May 03, 2006, 07:39:24 PM »
Is there any way to change a timer or counter set value through a logged on computer.

I can see that you can change variables and tiner present values using the edit command line e.g. TimerPV[11]=345, but I can't see how to change a set value :-[
A positive attitude may not solve all your problems, but it will annoy enough people to make it worth the effort.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3171
    • View Profile
    • Internet Programmable PLCs
Re:Timer Set Values
« Reply #1 on: May 03, 2006, 10:28:43 PM »
Right now the TRiLOGI does not implement the change of timer and counter set value in its "Edit variable" interface as the change is not immediately visible on the online monitoring screen. So to prevent changing the timer/counter value by mistake which can lead to problem, timer/counter cannot be changed from TriLOGI online monitoring.

However, you could use the host link command "Wm" and "Wu" you can change the timer or counter set value through TLServer "Serial Port Setup" screen.  That means user's own application program written in VB6 or VC++ can change the timer/counter SVs via the serial command.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS