Topic: RS-485 driver IC change (Read 11242 times)
CMS
Newbie
Posts: 18
I'm a llama!
RS-485 driver IC change
«
on:
August 08, 2006, 12:31:53 AM »
I remember reading somewhere the coms driver IC could be changed to provide better protection from network faults. Could you tell me where I caould find this information?
Thanks again
Logged
FQ-ONG
Jr. Member
Posts: 61
Re:RS-485 driver IC change
«
Reply #1 on:
August 08, 2006, 12:50:45 AM »
T100MD+ User's Manual (Green Cover):
Chapter 3:
Page 3-5:
3.2.2 Protection of RS485 Interface
Good Luck!
Logged
CMS
Newbie
Posts: 18
I'm a llama!
Re:RS-485 driver IC change
«
Reply #2 on:
August 08, 2006, 12:56:16 AM »
Thanks for that
I am sure I read that a substitute ic driver is available to do the protection internally. Perhaps I am thinking of another manufacturers PLC.
Logged
support
Global Moderator
Hero Member
Posts: 3174
Re:RS-485 driver IC change
«
Reply #3 on:
August 08, 2006, 09:57:47 AM »
It is LT1785AIN8 made by Linear Technology. It can withstand fault voltage up to +/-60V, whereas standard RS485 driver cannot withstand more than +12V or -7V. You can remove the existing RS485 driver and replace it with LT1785.
Logged
Email: support@triplc.com
Tel: 1-877-TRI-PLCS
CMS
Newbie
Posts: 18
I'm a llama!
Re:RS-485 driver IC change
«
Reply #4 on:
August 09, 2006, 01:34:50 AM »
Thats what I was after
Many Thanks
Logged