Author Topic: ADC VOLTS  (Read 12529 times)

philipjoseph

  • Jr. Member
  • Posts: 57
    • View Profile
ADC VOLTS
« on: October 26, 2003, 06:30:52 AM »
HI,
I HAVE A T100MD1616, I'M TRYING TO USE THE ADC TO SENSE THE TEMPERATURE USING A THERMISTOR 10K @ 25 C.

I CHECK THE VOLTS AT THE +5 VOLTS AND IT'S ONLY 1.2 VOLTS. I ADJUSTED THE AVcc POT BUT IT ONLY CHANGES FROM 0.5 TO 1.2 VOLTS.
I DON'T KNOW IF I HAVE TO CONNECT THE 24 VDC FROM THE POWER SUPPLY TO THE +12 to 24 V DC INPUT THAT IS BESIDE THE A/D IO TERMINALS.

THANKS
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »
Philip.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re: ADC VOLTS
« Reply #1 on: October 27, 2003, 06:20:38 AM »
For T100MD1616+ you need to provide the 24V analog power supply to its designated terminal. Please refer to the T100MD1616+ installation guide for details.
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS