Author Topic: md-exp1616r relay  (Read 12609 times)

jonsoderberg

  • Newbie
  • Posts: 3
  • I love YaBB 1G - SP1!
    • View Profile
md-exp1616r relay
« on: November 22, 2003, 03:05:40 PM »
I need to switch on a 120vac relay control loop on a soft start thyristor board.  Will I have to install a varistor/ bypass diode used for induction loads?? The load is minimal as its just a control circuit.
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re: md-exp1616r relay
« Reply #1 on: November 24, 2003, 01:40:03 PM »
What is the coil voltage? Is it a DC 24V or AC voltage? If it is DC 24V coil and driven by the solid state output from the PLC then no need to add diode as there is built-in flyback diode. But if you use relay output of the PLC then you should add a diode to absorb the inductive kick.

However, if your coil is 120VAC and you are using the PLC's relay output (that's the only choice) then you can use a varistor to absorb the inductive spike. But if the current to drive the coil is low then use of varistor is not necessary.
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS