Author Topic: T100MD+ Clock Frequency  (Read 11771 times)

Agradon

  • Guest
T100MD+ Clock Frequency
« on: July 28, 2004, 07:48:52 AM »
Does anyone know what the T100MD+ processor clocks at? I was unable to find this info in any of the manuals.

-Gene

Agradon

  • Guest
Re:T100MD+ Clock Frequency
« Reply #1 on: July 28, 2004, 08:52:15 AM »
Just found out that the processor clocks at 16 Mhz, finding out a little too late that the card is too slow for my application  :-\

Agradon

  • Guest
Re:T100MD+ Clock Frequency
« Reply #2 on: July 28, 2004, 09:05:39 AM »
The problem I am having is the fact that my application requires me to output at number to the PLC's outputs at a fairly high speed. I wrote the simplest program I could think of that would toggle one output bit on/off using the command "TOGGLEIO out1", "out1" being the name given to the pin output[1],0. I hooked up a probe to this output leading to an oscilloscope and ran the program, resulting in a peak speed of about  5ms per on/off cycle. With a 16 Mhz processor, the output should be able to update a lot faster then that, and I was wondering if there was any way of achieving this result.

Joel Moore

  • Full Member
  • Posts: 128
    • View Profile
Re:T100MD+ Clock Frequency
« Reply #3 on: July 30, 2004, 02:35:26 PM »
I'm not clear on what your app has to do but have you looked at the stepper or PWM outputs?  They can achieve some pretty high frequencies.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:T100MD+ Clock Frequency
« Reply #4 on: August 01, 2004, 10:51:23 PM »
The TOGGLEIO only toggle the memory bit inside the controller. At the end of the ladder logic scan the PLC has to update its entire I/O bank in an I/O refresh cycle. The I/O refresh implements software debouncing technique to filter out glitches that could be introduced by noise and the I/O refresh time takes approximately 2ms. That is the main reason that the PLC is unable to toggle an output quickly.  The minimum scan time of the PLC is therefore = logic scan time (approx. 10us per word) plus I/o scan time (minimum 2ms).

If you need to send out a fixed number of pulses, you may use the STEPMOVE command to achieve it.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS