Author Topic: Connecting PLC to Modbus Device  (Read 9837 times)

pardede

  • Newbie
  • Posts: 1
  • NoNe
    • View Profile
Connecting PLC to Modbus Device
« on: February 19, 2004, 06:54:12 PM »
Hello,
Can I connect modbus device (parity=0, Stop bit=2, Data bit=8) with the TMD+ ? as master?

TMD manual says, the modbus protocol use (no parity, 1 stop bit, and 8 data bit) which is different from the above device.

Thank you.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:Connecting PLC to Modbus Device
« Reply #1 on: February 20, 2004, 02:48:32 PM »
Yes, you need to use the SETBAUD command in a custom function to change the communication format to whatever your device supports.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS