Author Topic: Can no longer set PLC's Time from TriLogi 5.12  (Read 11291 times)

raan

  • Newbie
  • Posts: 31
    • View Profile
Can no longer set PLC's Time from TriLogi 5.12
« on: May 25, 2003, 06:41:14 PM »
Anyone
I was running the Trilogi web server 2.0 and was able to set the time on a T100MD888 using both the trilogi application and java applet. Now I cannot set the time through either approach. Anyone have ideas as to what may be wrong? However I still can set the time with the DOS application. I tried re-installing the Trilogi app and server but to no avail.
raan
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re: Can no longer set PLC's Time from TriLogi 5.12
« Reply #1 on: May 28, 2003, 06:53:05 AM »
1) Are you able to communicate with the serial port from within TLServer? Did you try the "IR*" command and what response did you get from the PLC?

2) Are you able to perform on-line monitoring, program transfer etc using Internet TRiLOGI?
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re: Can no longer set PLC's Time from TriLogi 5.12
« Reply #2 on: June 04, 2003, 01:08:56 PM »
We just realised that a bug in the TRiLOGI 5.12 software gives problem when you try to set the PLC clock on Sunday because the PC's real time clock gave a number 0 which was not handled properly by the software.  This will be fixed in the upcoming upgrade to version 5.2 (not yet released, should be soon).
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re: Can no longer set PLC's Time from TriLogi 5.12
« Reply #3 on: June 23, 2003, 03:12:19 PM »
We have released the TRiLOGI version 5.2. All licensed users can obtain free upgrade by following the "upgrade.htm" document in their CD ROM.
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »