Author Topic: reading current  (Read 9089 times)

karen

  • Guest
reading current
« on: March 08, 2002, 01:22:43 PM »
i have the 888+ is there any way to read current and display on the lcd the range is 0-100ma how or is it possible.  
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

Ken Talley

  • Guest
Re: reading current
« Reply #1 on: March 08, 2002, 04:30:08 PM »
Check with Leon, but I am pretty sure all you would have to do is some math to figure out what resistance you would need to convert the amperage signal to a voltage.  For example to convert the signal from 0-100mA to 0-5 volt you would put a 50 ohm resistor across the circuit in parallel.  You would then sample the voltage drop across the resistor with the 0-5 volt input on the plc.  This is making the assumption that I did my math right and the amperage you are measuring is in a current loop which should compensate for the load applied to the circuit to read it.  Again, check with Leon, but I think this will work.
Ken
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re: reading current
« Reply #2 on: March 08, 2002, 06:49:22 PM »
Ken would be right if the current that you are measuring is just a current loop signal that represent the numerical dimension of the measurand, and is not needed to do other work.  The 50 ohm resistor will become a "load" to the current loop signal that turns 100mA into 5V.

However, if your purpose is to measure the size of the current in a working circuit without introducing significant loading effect on the circuit, then an additional 50 ohm added to a circuit is probably unacceptable.  In this case, you will have to add a much smaller load, say a 0.5 Ohm resistor in series to the circuit. A 100mA current will generate 0.05V across the resistor and you will have to measure this small voltage drop using a differential amplifier that magify it by 100 times to get a 0-5V signal to the T100MD888+'s analog input.  - Leon  :)
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

karen

  • Newbie
  • Posts: 18
  • I love YaBB 1G - SP1!
    • View Profile
Re: reading current
« Reply #3 on: March 14, 2002, 02:42:10 PM »
thanks you are right Leon this is what i was looking for  can you recommend an amplifier that i can use

thank you

 ???
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re: reading current
« Reply #4 on: March 14, 2002, 03:29:43 PM »
I am not an expert on OpAmp. But I think a low cost 741 will probably do the job. I would like to refer you to a document found on the following weblink:

http://www.oldradio.de/service/uel/reports/anel/opamp741.pdf

- Leon
« Last Edit: December 31, 1969, 04:00:03 PM by -1 »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS