Hi,
I am new to the i-Trilogi PLC. I have just bought an i-7018 module to connect 4 thermocouples. I have questions how to connect the module to F1616-BA PLC.
1. The manual has mentioned that I have to turn on Init, but in the module, there is no INIT switch. So what do I need to do to set it up?
2. I connect my laptop to F1616-BA PLC module via Ethernet connection and connect i-7018 to the RS485 COMM3 of the PLC. In the manual it is not clear how to connect the module to PLC and the laptop. So when I run the DCON utility, it cannot find the i-7018 module. Does the connection correctly set up? How can I configure the i-7018 module via Ethernet?
3. After finishing the connection, how to call the value of each thermocouple in the i-TRILOGI program?

Thanks,
« Last Edit: December 30, 2015, 07:31:46 AM by ttadsana »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:Need info how to connect i7018
« Reply #1 on: December 30, 2015, 11:59:08 AM »
Do you have a USB to RS485 converter? You will need that in order to configure the I-7018 module using the DCON utility.

Basically you use a PC to configure the I-7018 via the RS485 port. The main purpose is to configure it to the correct baud rate settings as that of the PLC (default is 38400, 8, 1, n for the PLC but 9600, 8, 1, n for the I-7018). If you only have one I-7018 module then you can keep the default ID. If you have more than 1 I-7018 then you will need a different ID for each module.

Once you have configured the DCON to be the same baud rate as the PLC, then you simply connect the RS485+ of the PLC to that of the I-7018, and similarly for the RS485-. Assuming the I-7018 and PLC share the same 24V power supply that's all the connection that is required (two wires).  

However, if the I-7018 and the F1616-BA are using different power supply then you should connect their 0V together to provide a common ground.

You can then refer to the sample programs in the following i-TRiLOGI folder:

C:\TRiLOGI\TL6\usr\samples\I-7000

Inside this folder you should find the sample program I-7018.PC6 which you can transfer to the PLC and then observe for the response from the I-7018 and the value displayed on the PLC's LCD (if you don't have the actual LCD you can go online monitoring of the PLC and click "View" button to see the virtual LCD on the online monitoring screen.

If there is problem in the communication, you can connect the USB-RS485 converter to the RS485 pairs and run a terminal emulation software (e.g. RealTerm) to monitor the communication. Since the COMM is via ASCII text you can see what the commands sent from the PLC and check for the response from the I-7018.





« Last Edit: December 30, 2015, 01:23:14 PM by support »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

ttadsana

  • Newbie
  • *
  • Posts: 2
  • I'm a llama!
    • View Profile
Re:Need info how to connect i7018
« Reply #2 on: December 30, 2015, 01:08:21 PM »
Hi,
Thank you very much for answer. I do not have a USB-to-RS485 converter. If so, I will get it to be able to configure the i-7018 module. I will try.

Thanks and Happy New Year.