Author Topic: FMD88-10 HSC  (Read 13106 times)

cch1955

  • Full Member
  • Posts: 198
  • Automated Machine Systems Designer
    • View Profile
FMD88-10 HSC
« on: December 23, 2015, 04:21:23 PM »
I need to use the HSC to count a single channel square wave input without a second input in quadrature. The frequency of the count is 2000Hz maximum.

How can this be done. I willing to give up the phase B input line.

How can this be done?

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:FMD88-10 HSC
« Reply #1 on: December 23, 2015, 04:48:46 PM »
Just define a HSCDEF channel and by default the channel will count up if phase B is held at OFF.

E.g. for FMD88-10, input #3 and #4 forms a quadrature channel. By default without forcing into enhanced quadrature, the HSC will count up when input #4 is OFF and pulses coming into input #3.

Alternatively, if input #3 is held at OFF and pulses come into input  #4 then HSCPV will decrement.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

cch1955

  • Full Member
  • Posts: 198
  • Automated Machine Systems Designer
    • View Profile
Re:FMD88-10 HSC
« Reply #2 on: December 28, 2015, 12:59:26 PM »
Good to know this for single channel HSC needs, thanks.