Author Topic: fX2424 ENCODER INTERFACING  (Read 12308 times)

cch1955

  • Full Member
  • Posts: 198
  • Automated Machine Systems Designer
    • View Profile
fX2424 ENCODER INTERFACING
« on: September 08, 2014, 04:15:09 PM »
I have an 12-24 VDC supply encoder with NPN outputs that I want to use with a Fx2424 PLC. What is the value of the internal pull up resistor on the Fx2424 inputs to 24VDC which the encoder will have to pull low?
Thanks

 

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:fX2424 ENCODER INTERFACING
« Reply #1 on: September 08, 2014, 11:34:49 PM »
The inputs on Fx2424 are are pulled up to 24V DC via a 5.6K resistors.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

cch1955

  • Full Member
  • Posts: 198
  • Automated Machine Systems Designer
    • View Profile
Re:fX2424 ENCODER INTERFACING
« Reply #2 on: September 09, 2014, 08:18:41 AM »
Thank you for the prompt reply.