Author Topic: EXP1616R extension with FMD88-10  (Read 11040 times)

Philippe Parmentier

  • Newbie
  • Posts: 29
  • new in plc
    • View Profile
EXP1616R extension with FMD88-10
« on: March 07, 2014, 03:54:14 PM »
Good day everyone,

I've set a EXP1616R to an FMD88-10 and I had problems to use input and output #9 to #16
but it's seems to start at #17.
I guess it's due to 16bits aligments.

I was using the SETSYSTEM 16,3 command to scan only the first 8x3 I/O and speedup the ladder loop.

Due to what i've noticed, I set SETSYSTEM 16,4 to scan the first 32 I/O, but on the EXP1616R the last Output (#32) was always closed even if it was not in the Ladder logic.

I've then set to SETSYSTEM 16,5 and it look like working well. Is it a normal behaviour?

Regards


support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:EXP1616R extension with FMD88-10
« Reply #1 on: March 07, 2014, 11:57:48 PM »
We have  tested and found that SETSYSTEM 16,n  require n to be >= 3, and you are right that in order to support up to 32 I/O n has to be > 4.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS