E10 limitations
« on: May 10, 2013, 09:07:46 AM »
Hello,

Sorry for yet another E10 question.
I've seached the web site, documentation and these forums but have been unable to locate the information I am looking for regarding the limitations on the E10.

I am sure its there somewhere but I cant find it.

I know that there is a limit of 4 timers on an E10 but what is the limits for counters? Is it the same? The reason I am asking is I need just 1 extra counter. I have 4 counters but when I add a 5th my program fails to work

The funny thing is, if I leave the 5th counter in the counters list (F2) but just remove all of the references to it in the ladder then the simulation works.

If I then do a simple ladder rung like:
--||--------()          Input 1 normaly open, through to counter5 coil.
Then the program will not launch simulation. Ctrl+F9 and nothing happens
Simulate -->> Run (All I/O reset) and again nothing happens.

If I remove the offending rung, the simulation runs and I can see the 5th counter listed (even though nothing references it in the ladder).

Are my issues related to a limit of 4 counters?

Thank you.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:E10 limitations
« Reply #1 on: May 11, 2013, 10:04:12 AM »
Yes, E10 is limited to 4 timers, 4 counters, 8 internal relays.

For a small PLC with orders of magnitude more powerful than E10, try the Nano-10. You have 64 timers, 64 counters and lots of variables that can be used as additional counters.
« Last Edit: May 11, 2013, 10:33:17 AM by support »