Author Topic: Could RS232/RS485 jumper in wrong position damage the COM port of E10?  (Read 11205 times)

kpskps

  • Newbie
  • Posts: 2
    • View Profile
Hello,

I started experimenting with the newly arrived Nano, E10 and the old T100MD+

I set up the RS485 network with all three. Used U485 to connect to PC.

Using U485 configured Nano to address 00
Using Serial cable, configured T100MD+ to address 02
Address of E10 left it unchanged at 01

When I checked one by one, E10 was not responding to the @01RI00* command. Others were responding (to @00RI00* and @02RI00* respectively).

Then I realized I had not changed the jumper. Changed it to RS485 position. Still no response.

Checked connections. All OK ( D+ to pin 5 and D- to pin 2).

Then I switched back to testing directly with serial port. Again no response. Then I realized I had not reverted the jumper setting to RS232 position. Changed it. Still no response.

E10 is functionally ok. It is running its sequencer program which I loaded earlier through RS232. Problem is only with communication.

As narrated above, the  only sin I seem to have committed is to try RS485 communication with jumper in RS232 setting and once again trying RS232 communication with jumper in RS485 position.

Could this possibly damage the COM Port?
If so, what is the remedy?

What else could be wrong?

Regards,
kpskps


kpskps

  • Newbie
  • Posts: 2
    • View Profile
Issue resolved.

Problem was with the baud rate.
E10 default baud rate is 9600.
Had to change it to 38400.

kpskps

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Spot on!