Author Topic: Nano-10 down load  (Read 11151 times)

cch1955

  • Full Member
  • Posts: 198
  • Automated Machine Systems Designer
    • View Profile
Nano-10 down load
« on: April 07, 2011, 03:24:43 PM »
I have a Nano-10 that I need to down load a program from my PC vis the USB - RS485 adapter. I dont see any instructions on what program to run to support this. Please supply link to instructions for this. I have CD with TL Server 3.15 and Trilogi 6.3.

Also if I only have single PLC connected to RS-485 on Nano-10 do I need terminating resistor? If so what value?
Thx

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:Nano-10 down load
« Reply #1 on: April 07, 2011, 08:44:46 PM »
The instruction are actually in Chapter 3 of the i-TRiLOGI Programmer's Reference (http://www.tri-plc.com/documents/TL6ReferenceManual.pdf ) . You need to run TLServer, test the COM port settings to make sure that you communicate with the PLC via the RS485 port. After that you just use i-TRiLOGI to communicate with the localhost server at 127.0.0.1:9080. The rest are the same as communicating with the PLC via Ethernet port.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS