Author Topic: Locked Out  (Read 5138 times)

rcsystems

  • Newbie
  • *
  • Posts: 2
  • I'm a llama!
    • View Profile
Locked Out
« on: January 02, 2011, 11:08:23 AM »
Hi I seem to have locked myself out of my Nano-10 by changing the access level to User inside the "ethernet and ADC config" page. I can no longer transfer programs to my PLC :(

Help!!

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3171
    • View Profile
    • Internet Programmable PLCs
Re:Locked Out
« Reply #1 on: January 02, 2011, 12:09:00 PM »
Are you still able to access the Ethernet and ADC Config page from Ethernet? If not, then you have to access it from RS485 port.  In this case you need to run TLServer and use the Localhost address instead of PLC IP address to access the Nano-10 and reset the configuration.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

rcsystems

  • Newbie
  • *
  • Posts: 2
  • I'm a llama!
    • View Profile
Re:Locked Out
« Reply #2 on: January 02, 2011, 01:50:32 PM »
Thank you for your help!

I was able to access it over Ethernet but that would not let me edit the config.

RS-485 allowed me to do it.

Thanks again!