« on: September 23, 2010, 08:56:04 PM »
Hi, I'm new to tri-plc, I purchased the T100MD

Is it possible to increment data registers using ladder only?.

EX:

-| |----------------------------------------- INC DM[1]

Or does a custom function have to be used to change values in data registers?.

Thank You

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:data registers
« Reply #1 on: September 23, 2010, 11:01:50 PM »
Yes. You have to use custom function and TBASIC to change variable such as DM[].

To use ladder logic only you can increment a counter using the [UpCtr] function. If your range is from 0 to 9999 this will work. You can read the counter value inside a custom function by referring to it as CTRPV[n].