Motor control
« on: July 28, 2010, 09:18:45 PM »
Hi. Has anybody tried to control the speed of an ac servo motor by using the analogue output to give a voltage to the motor driver? I currently have a motor driver that accepts 0-10vdc as analogue input. I want to use the analogue output of 0-5vdc to control it. The question is that if I activate function setDAC 1,4096, will the motor driver immediately run at full speed? Or should I write a function to accelerateor decelerate the motor by varying the output voltage?

Regards
Can

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:Motor control
« Reply #1 on: July 29, 2010, 09:16:43 AM »
A servo motor should have its own feedback loop so you can simply supply it with a stable voltage it needs.

Since the servo motor driver requires 0-10V you need to give it 10V to run at full speed. You can use the F1616-BA which has built-in 0-10V analog outputs.

If you supply 5V to the servo motor it is most likely going to run only at half speed (depend on what the spec is).



Email: support@triplc.com
Tel: 1-877-TRI-PLCS

can

  • Full Member
  • Posts: 160
  • I'm a llama!
    • View Profile
Re:Motor control
« Reply #2 on: July 29, 2010, 09:28:25 AM »
Hi. So do I have to varies the DAC from 0 to 4096 if i want the motor to accelerate smoothly?

Regards

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:Motor control
« Reply #3 on: July 29, 2010, 09:30:41 AM »
I don't think so, but there is nothing to stop you from doing it. The best is to test the dynamic of your system by using a step input first (i.e. apply the voltage in a single step) and if the response is not desirable you can then give it a slope which is easy to do with our PLC.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

can

  • Full Member
  • Posts: 160
  • I'm a llama!
    • View Profile
Re:Motor control
« Reply #4 on: July 29, 2010, 09:31:45 AM »
Ok. Thanks for the quick reply. Will try that out.

can

  • Full Member
  • Posts: 160
  • I'm a llama!
    • View Profile
Re:Motor control
« Reply #5 on: July 31, 2010, 12:22:32 AM »
Hi. I have another question. If the servo motor driver output is giving positional signal by A, B, and Z phase, is there anyway a 888 will be able to determine the position by reading the signal?

Regards

support