Author Topic: not able to connect to E10  (Read 5768 times)

andy22

  • Newbie
  • Posts: 2
  • I'm a llama!
    • View Profile
not able to connect to E10
« on: February 05, 2010, 03:37:51 PM »
Hello,
I have a problem with the connection to a E10NPN

cable must be Ok because I can communicate with the T100MD
as software I have WinTrilogi v 3.52

Can You please help me,  
Thanks in advance
andy

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3171
    • View Profile
    • Internet Programmable PLCs
Re:not able to connect to E10
« Reply #1 on: February 05, 2010, 03:48:40 PM »
Did you got to the "Serial Port Setup" and select the correct COM port?  E10-npn default baud rate is 9600 bps, 8 data bit, 1 stop bit and no parity. Try to enter "IR*" at the command box and if you get a response such as "IR01*" then the communication is OK.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

andy22

  • Newbie
  • Posts: 2
  • I'm a llama!
    • View Profile
Re:not able to connect to E10
« Reply #2 on: February 05, 2010, 03:52:49 PM »
WOW

Thanks very much, it MOVES

Andy